Externally summed CTs for bus protection 3
Mbrooke
Starting this not to steer off another thread, but I inquire 2 questions:
1. At what point or fault levels do engineers typically move away from externally summed CTs for (over-current) bus differential protection? C800 class CTs of concern here FWIW.
2. Can externally summed bus protection CTs be used in networked circuits?
Our local DisCo had adapted the fast bus trip scheme for new installations. Previously a High Z (GE PVD) scheme was used. SEL has a nice explanation of the scheme in the 251 Manual, along with a scheme that allows the bus relay to handle a failed feeder relay, or a feeder relay OOS for other reasons. There is a bit of wiring involved, so this is on new relay panels / switchgear.
I can confirm from commissioning these schemes, the 3 cycle time (between relays) is easily achieved.
After my adventures of the past few days I am so terribly glad that our dabbling in the 251/251C fast bus scheme was a brief episode and that we've long since moved into a more enlightened era of dual feeder relays, bus protection, breaker failure logic, and a maintenance mode switch on the transformer protection. It's all been SEL from then till now, but that fast bus trip era was truly a misguided, penny wise pound foolish, attempt at getting more that what you were willing to pay for. SEL had this great idea how you could get more out of fewer relays; they sold fewer relays and we got worse results over the long run. There's no free lunch.
That scheme has some obvious advantages and it was well sold; but that was 20 years ago. There are some very subtle ways for it to fail; at the moment I don't feel that sharing would be appropriate but it seems to have built in several traps. Don't (just) look at first cost; look at the costs (both tangible and non-tangible) of an extended outage simply because some corner case behaves radically differently from what everybody is more familiar with.
jghrist said:
You need to look at the burden and the system X/R ratio as well as the fault current to determine saturation.
Vs = (1+X/R)·If·Zb
I would recommend low impedance with restraint or high impedance. If you are concerned about cost, consider a fast-bus trip scheme instead of bus differential. If you have microprocessor relays on the main, bus tie, and feeders, you might achieve 3 cycle operation without any additional relays or CTs.
I know long runs in the CT circuit (higher ohms) decrease saturation, but, how does low burden play into this?
Thanks, a wealth of wisdom as pure usual :) Considering your experience, practicality and advanced knowledge in the field of protective relaying I am going to take your word on fast-bus. Having decentralized bus bar protection for 12kv and above has never sat right with me, I actually prefer having more relays.
If you feel comfortable saying, what do you use for bus protection at the 12-34.5kv levels?
At that level we're using the 587Z plus optical arc flash detection plus a maintenance mode switch on the transformer protection. We go that route in part because some switchgear would require three 487Bs, one per phase, to cover the 8 or 9 breakers and there's no place to mount all of those. Anything transmission gets redundant 487Bs.
Sounds like a well thought out practice. :) On the 487Bs, you've never had any inadvertent operation from saturated CTs, correct?
David, nice comments.
The problem with that scheme with the 251 is that it keeps cropping up as a way to save money.
What I don't find is papers on how to best install the fibers for arc-flash protection.
I can't recall any misoperations of a 487B, neither over tripping nor under tripping, on our system
Ok, guess I need a course on factors increasing CT saturation. Any good links or papers on the subject?
Stan Zochall's CT book available from SEL would be a good start.
Also anyone know how to find the line angle on a distribution bus?
Third book on
Appears to also be available through Amazon.
Why would you need a "line angle" for a bus? I imagine that you could calculate the impedance as though the bus were a line and use that. Pretty sure you'll get something over 80 degrees.
The first paper makes not of line angles and CT saturation on page 3, which threw me off.
And oh, thank you for the link. Much appreciated :)
You can calculate X/R from the line angle. You need the fault current in complex form to get X/R or the line angle. Line angle = arctan (reactive part of fault current / real part of fault current). X/R = tan ( line angle). For a distribution bus on the load side of a power transformer, the X/R ratio is high because most of the fault impedance is the transformer which has a high X/R ratio.
I take it 3 paralleled 30/40/50 MVA 115-34.5kv transformers will produce a very, very high line angle?
Yes. Hopefully you should be able to get the fault X/R from your system model by applying a 3LG fault on the bus.
I have the transformer R and X for each unit, plus the source 115kv impedance. Will this be enough?