Field Weakening Point

Status
Not open for further replies.

MAGTiger

Electrical
Apr 30, 2008
107
Can someone explain the significance of the "Field Weakening Point" parameter in VFD's?

Thanks

Neil
 
Replies continue below

Recommended for you

For normal field strength and constant torque capability, the ratio of the output voltage to output frequency (V/Hz) is nominally constant. At output frequencies above the field weakening point, the V/Hz and (thus the field strength) is reduced as the frequency increases. Usually, that is the point at which the nominal output voltage is equal to the nominal input voltage and the VFD doesn't have the capacity to keep increasing voltage with further increase in frequency.

With field weakened operation, the torque capability is reduced as the frequency (speed) increases. In comparison to speed, the torque capability drops more rapidly than the drop described by a constant horsepower torque vs. speed curve. However, constant horsepower operation can be maintained up to some point like 150% of base speed or so.
 
Thanks, that's what I kinda thougt, just wanted to be sure.

Neil
 
What kind of VFD are you using Neil? I'm sort of canvasing for ones that provide it. Many have really truncated abilities to allow you to set it.

Keith Cress
kcress -
 