Hello Everyone,
Please how do you find the earth fault at the load side where you need to connect an RMU only at the load side?, the Resistance of the combined HV/LV earthing system(TN-C) can be taken as ≤10 Ohms. The available data I have from the source substation are:
1. 11kV Fault level - Three phase fault (6777A)
Earth Fault (987A)
2. Earth Resistance - Calculated(0.16 Ohms)
Measured (0.13 Ohms)
3. Cables connecting source to load side - 3c 0.3in² PILCSWA (Al) @0.965km
3 x 1c 150mm² EPR (16mm² screen) @0.122km
3 x 1c 70mm² EPR (12mm² screen) @0.402km