The pre-pour test results per ASTM C 1260 is coming as 0.14%. The specimen prepared was without flyash. This value is beyond 0.10%, which is the acceptable limit. The concrete pour is coming up in less than a month. The actual concrete mix will have flyash in it. Is there a way 0.14% value could be bought-off? Are there other tests which could be carried out to test the reactivity? FYI-the same testing agency gave a value of 0.03% few months back for the same set of fine aggregate. The difference in results perplex me. What is the best way out?
Info on concrete mix:
w/c ratio = 0.31
HRWRA will be used
Cement Type I/II will alkali < 0.6%
Coarse aggregate passed the alkali-silicate reactivity test.
Flyash is more than 15% as compared to cement content.
Appreciate your input on this.
Thank you,
Sushil, PE
Nebraska
w/c ratio = 0.31
HRWRA will be used
Thank you,
Sushil, PE
Nebraska