Fire Case - Tank Area 1
Bill3752
Chemical
For a horizontal tank that is more than 1/2 full (say 2/3), what area should be assumed to be exposed to a fire from below? Only the bottom half? Thanks, bill
The area exposed to Fire corresponds to the liquid level in the tank.
If the level is 25%, the wetted area corresponds to 25%.
One has to ajust for liquid swell.
If the level is 25% AT AMBIENT, the level will expand at actual relief temperature.
Something like hexane can expand alot and can cause problems.
If one starts with 85% level, the swell may expand to 95-100%. Two-phase flow calculations would be triggered.
Thanks, so the bottom line is that I should assume the fire will hit the top of the tank also.
To bring this to a conclusion then, if I have a vertically mounted cylinder that is completely full, I should count the very top of the tank in the area calculation? For the sake of discussion, forget about swelling and two phase flow.
Yes and also include the top head if liquid resides inside the head.
There is a concept of flame height associated with wetted area.
The exact flame height depends on standard being used.
I believe API uses 25-ft for low hazard process areas and 50-ft for high hazard process areas.
For tank farms 30-ft flame height is used.
Eurpoean folks use 10-meters.
NFPA has something different depending on the situation.
If the bottom of a 10-foot verticle tank was 23-ft above grade, the wetted surface would correspond to 2-ft assuming the 25-ft flame height standard
You should also review API 2000 and NFPA 30. Wetted area is the internal area of the tank that can be wetted by the stored liquid. I would not be comfortable with a design based on filling a tank to a given percent volume - you should instead base your vent flow rate on the available volume of the tank.
Dear Yitbos,
You said "Eurpoean folks use 10-meters". COuld you please give us your source?
"We don't believe things because they are true, things are true because we believe them."
Ditto on the 50 foot for API "high hazard process areas." The only API 520/521 flame height I'm aware of is 25 ft above a surface that could conceivably contain a pool of flammable material (thus supporting a pool fire).
Bill,
If you are a subscriber at Che.com [or receive Chemical Engineering Magazine] there is a great article for calculating wetted areas for partially filled horizontal vessels.
Doane, R.C. "Accurate Wetted Areas for Partially Filled Vessels." Chemical Engineering Magazine, December 2007. pp 56-7.