Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Fire protection for hydroelectric plant tunnel under construction

Status
Not open for further replies.

jejaram

Electrical
Feb 9, 2011
45
Hi

What could be used as fire protection in a tunnel under construction? I guess portable extinguishers, but how far apart should they be placed and how do you fix extinguishers to solid rock?

The tunnel is for a hydroelectric plant, so the tunnel will be filled with water once the plant starts generating, so a permanent system wouldn't be practical.

There are not many things inside that could burn, but there are lamps that could cause short circuits and ventilation systems that could burn as well as cables.

Is there a code for this? I checked the UK tunnel code I have access to (first edition) and it doesn't mention anything. NFPA 10 wasn't developed for this type of conditions, so i don't know where else to look.
 
Replies continue below

Recommended for you

Look up MSHA. They cover mines. You not digging a mine but a fire is a fire. I am sure they cover combustible material, lighting, communication and breathing devices.
 
Hello!

Good day!

As mentioned, the project is a Hydroelectric Power Plant.

I suggest you go through NFPA-851(2010) & NFPA-850 (2015). These recommended practice are good start.

NFPA-851 chapter 8 (Fire Protection for the construction Site)


Hope this helps,

PAtrick

 