fire Protection system for oil storage tank bund wall
kald
Petroleum
Feb 26, 2003
47
How to design fire Protection system for oil storage tank bund wall ? , what is the minimum requirements , standard , procedure to follow ?
I do not believe that the bund wall itself needs fire protection... I have never seen this in a code or standard
The bund spends 99.99999% of its time doing nothing.
Is this your question ?
MJCronin
Sr. Process Engineer
Actually, I found some companies standard required to install hydrant at bund area each 9 m and other required monitor
so I ask I there is any international standard for that
mk3223 said:
The tank bund area sizing for the oil tank can be based on NFPA 30, Flammable and Combustible Liquids Code.
I search in it, but I didn't found any refer to fire protection for oil storage tank bund wall
Areas inside the bund walls may be protected with foam monitors for spillage inside the area depending on type of liquid and other factors. You will need to check either your client requirements or the insurance carrier standards as suck installations are typically regulated by these two bodies.
Many thanks
Also avoid any penetrations of the bund wall as this creates week points where you need to ensure fire protection to stop the bunds leaking during a fire.
Read up on Buncefield for issues due to bunds leaking during a long fire.
nfpa 30 or nfpa 11/ 16 for monitor coverage....the design intent is cooling of adjacent tank shells if you only have a fire water loop ...it theres foam also then you would be assuming you have a tank or tanks with open top/ EFR/geodesic dome/ or frangible roofs. ...even then you will still have a cooling water requirement...fixed monitors portable foam cannons, hydrants etc spaced as the code requires for versatility of tactics.
the intent of your fire system in a tank farm is at a minimum to control until burn out and ensure that the individual hazard does not compromise the integrity of adjacent structures, tank walls etc and that the equipment continues to perform as intended until the emergency has been mitigated....yes life safety too.....but no one is hanging out in the tank farm
in one of these nfpa codes the provide coverage density guidelines which you use along with your tank shell surface dimensions to come up with the GPM needed to cool and maintain the tanks structural integrity when there is adjacent flame impingement. there are also requirements that you are able to provide the required cooling water flow to the surface in question from 2 different points (or is it 3...?) around the wall.
that said , these coverage density values stated are assuming the shell to shell spacing at a minimum meets the separation requirements stipulated in NFPA 30
@littleInch
in addition there is a required 2 hr minimum fire rating for the containment ...this would apply to the sealing methodology around any penetration's...
The problem with that is that a pool fire in the bund lasts a lot longer than 2 hours...