kald
Petroleum
- Feb 26, 2003
- 47
How to design fire Protection system for oil storage tank bund wall ? , what is the minimum requirements , standard , procedure to follow ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
MJCronin said:I do not believe that the bund wall itself needs fire protection... I have never seen this in a code or standard
The bund spends 99.99999% of its time doing nothing.
Is this your question ?
I search in it, but I didn't found any refer to fire protection for oil storage tank bund wallmk3223 said:The tank bund area sizing for the oil tank can be based on NFPA 30, Flammable and Combustible Liquids Code.
Many thanksUFT12 said:Areas inside the bund walls may be protected with foam monitors for spillage inside the area depending on type of liquid and other factors. You will need to check either your client requirements or the insurance carrier standards as suck installations are typically regulated by these two bodies.