Fire protection 1
shonuff
Industrial
Aug 15, 2013
20
Can anyone suggest the proper code or standard to follow for plant firewater piping(psv, monitors, valves, etc) inspections? Would it be NFPA 25?
Before embarking on such research, discuss the situation with your fire insurance carrier, otherwise, you may be off on your decisions and then be denied credit on your fire insurance policy.
See
NFPA 24 for fire service mains.
NFPA 13 for sprinkler system
NFPA 14 for standpipe
NFPA 20 for fire pumps
There is an NFPA forum dedicated to this in the engineering codes, standards and certification section...
My motto: Learn something new every day
Also: There's usually a good reason why everyone does it that way
Hi Shunoff
There are a lot of NFPAs, the ones that I've used on tank farms so far are:
NFPA 11 - Standard for Low Expansion Foam
NFPA 13 - Installation of Sprinkler systems
NFPA 16 - Standard for the Installation of Foam-Water Sprinkler and Foam-Water Spray Systems
NFPA RP 14G - Recommended Practice for Fire Prevention and Control on Open Type Offshore Production Platforms
NFPA 20 - Standard for the Installation of Stationary Pumps for Fire Protection
NFPA 22 - Standard for Water Tanks for Private Fire Protection
NFPA 25 - Standard for Inspection, Testing and Maintenance of Water-Based Fire Protection Systems
NFPA 30 - Flammable and Combustible Liquids Code
NFPA 58 - Standard for the Storage and Handling of Liquefied Petroleum Gases
You can also make use of IP19.
Hope this helps!
Gareth