I have a vessel with lots of large bore liquid pipework within a fire area.
I want to confirm the correct option for gire heat input as per the API 521 equation. Is it
Option 1: calculate total wetted surface area then do A^0.82
Or
Option 2: calculate A^0.82 for all pipes and vessels individual and sum them.
Option 2 results in significantly larger fire heat inputs but im worried it is overly conservative or even wrong.
Thanks.