fire sprinkler shut off at top of elevator shaft.

Status
Not open for further replies.

cdafd

Specifier/Regulator
Aug 18, 2005
2,936
I do not think it is used or used much.

But, I am just trying to find either the piping diagram or a picture of the shut off, on the outside of an elevator shaft.

I forgot along time ago where I did see it. I thought it was in the old 13, but maybe something else??

Thanks
 
Replies continue below

Recommended for you

Butterball valves are commonly used for protecting elevator shafts. Typically you'll see a flow switch with zero retard as well.
 
I was trying to find the pipe diagram

Or a link to a picture of one installed
 
We use them quite a bit. Especially since I cannot get a clear answer from the elevator types on belt/cable composition. I therefore default to combustible.

Not sure there has ever been a diagram in 13 or other codes. Might be something you saw on a plan or the like.

Each one is different, but basically it is just 1" pipe, with a tampered "Butterball" in-line.

I might could scrape up a pic of one of ours...

R/
Matt
 
Thanks

Maybe I have just been around fire sprinklers to long.
 