I work in a facility with dozens of air handlers and fans.
If one of the buildings goes into fire mode due to smoke detector alarm all the AHUs shut down as per the control strategy for that building.
When the fire trip is cleared back at the main Fire Panel (usually after a fasle alarm) some of the air handlers come back on automatically, some require resetting at the MCC panel and others require resetting at the BMS... a propper mess as you can imagine, when this does occur.
What should the proper reset strategy be in your opinion?
Regards
REMP
If one of the buildings goes into fire mode due to smoke detector alarm all the AHUs shut down as per the control strategy for that building.
When the fire trip is cleared back at the main Fire Panel (usually after a fasle alarm) some of the air handlers come back on automatically, some require resetting at the MCC panel and others require resetting at the BMS... a propper mess as you can imagine, when this does occur.
What should the proper reset strategy be in your opinion?
Regards
REMP