thkurian
Mechanical
- May 18, 2015
- 16
Hi,
We have a motor driven horizontal split casing (BB1)fire water pump in a new project under construction with rated capacity = 1136 m3/hr, Head = 131.5 m, Motor rating = 780 kW. As per NFPA 20, only a 1" relief valve is provided for minimum thermal flow. As per NFPA 25, pump is to be tested at non flow (only 1" relief valve is open) weekly for 10 minutes. Is this an acceptble practice for such high capacity pumps? Why a non-flow test is specified by NFPA 25 with 1" relief line instead of a separate test line with full pump capacity? In this project a separate test line is provided connected to suction tank which allows weekly pump testing at rated capacity. Please advise we can waive nonflow test as per NFPA 25 and conduct pump test at rated capacity for weekly run using test line.
Regards
Thomas Kurian
We have a motor driven horizontal split casing (BB1)fire water pump in a new project under construction with rated capacity = 1136 m3/hr, Head = 131.5 m, Motor rating = 780 kW. As per NFPA 20, only a 1" relief valve is provided for minimum thermal flow. As per NFPA 25, pump is to be tested at non flow (only 1" relief valve is open) weekly for 10 minutes. Is this an acceptble practice for such high capacity pumps? Why a non-flow test is specified by NFPA 25 with 1" relief line instead of a separate test line with full pump capacity? In this project a separate test line is provided connected to suction tank which allows weekly pump testing at rated capacity. Please advise we can waive nonflow test as per NFPA 25 and conduct pump test at rated capacity for weekly run using test line.