SteelPE
- Mar 9, 2006
- 2,759
I have a project where I have to calculate the capacity of an existing wood framed floor (should be simple enough). I made a visit to the site yesterday and took a few photos and took some measurements. I noticed that all of the floor joists were notched in order to rest on a flush framed wood beam (see photo).
The notches on these joists is over the allowable notch located in the building code (which I believe to be 10% of the overall depth of the wood member). NDS does give an allowable shear equation for notches of fv = [3V/2bdn][d/dn]. Using this equation I am calculating an allowable end reaction of 154# which gives me next to nothing in capacity for the floor (17.5 psf).
I know this method of construction was used in the 1970's (my parents house has this exact detail). Question is, do I ignore the detail based upon it's the historical use of the detail or do I report the capacity of the floor as 17.5 psf? I am leaning towards the 17.5 psf as it's really not my problem to deal with at this time.