StrEng007
- Aug 22, 2014
- 535
TLDR: The Florida residential code requires thicker plywood roof panels than the Florida building code. I cannot tell if this is due to one being prescriptive while the other is analytical. I'd like to get some feedback from other Florida engineers.
Detailed discussion:
I wanted to confirm with the other Florida practicing engineers out there, it appears as though the 2023 FBC Residential general provisions have more conservative restrictions than the 2023 FBC Building HVHZ regarding roof wood structural panels.
Per the Building Section 2322.2.3, the minimum nominal thickness of roof sheathing is set at 19/32". Additionally, for a roof with truss framing at 2 FT o.c., the panel span rating must achieve 32/16. Per the APA, a panel span rating of 32/16 corresponds to a performance category of 15/32" thickness. So you basically have two criteria:
•Use 19/32" as a minimum (GOVERNS)
•Based on truss spacing, 15/32" is allowed
Per the Residential Section R803.2.2, the minimum performance category and span rating is determined based on wind exposure and wind velocity. Per Broward and Miami-Dade building jurisdictions, the design wind speed for typical residential structures is 170 to 175 MPH, with wind exposures C and D (varying distance from the coast).
Take a residential building in Miami, with V=175 MPH at exposure C. The required performance category defaults to 23/32" with a span rating at 48/24. In this situation, both the span rating align with the typical performance category.
So by default, any plywood used here cannot be less than 23/32" thick.
What's interesting is the Residential code requires a more conservative approach. Is this due strictly to the prescriptive or analytical methods? Meaning, does the Building code section assume there is an engineering analysis taking place while the Residential code assumes the spec is prescriptive? Sometimes I have difficulty understanding when the code is setting a prescriptive measure or setting a minimum check against an analytical approach.
Also, how many of you specify 19/32" or 23/32"? I'm used to specifying 5/8" or 3/4".