Hi Friends
I have been asked to check how the system will perform if 25% of the cooling capacity is lost.
The system is in design stage and the system sizing considering all units operating is as follows
Plant Configuration : 4 x 125 KW
Ambient : 44 deg C/90% RH
Installed Total Load : 500000 Watts
Coil SHR : 0.631
Coil Sensible Load : 315500 Watts
Coil Latent Load : 184500 Watts
Air Flow over the Coil: 23172 l/s
Fresh Air : 1158 l/s
Return Air: 22014 l/s
Off Coil DB : 14 deg C
RH : 90%
Supply Temp DB 15.5 deg C ( 1.5 deg C heat gain ssumed)
RH: 82.1 %
Room Actual Cond : 24 deg C
RH : 50%
RSHR : 0.92
Is there any way to check what would the room conditions if 25% capacit is lost (all others like air flow, room loads etc remain same). I have attached the Psy Chart.
Thanks