Zaman01760 - When you ask about Procedure are you referring to describing the physical act of installation, or the analysis necessary to determine what should be done, or both?
The "Procedure" depends on a number of factors:
[ul]
[li]Completed floor(s)' strength(s) at each stage of construction load application(s).[/li]
[li]Formwork & shoring system used.[/li]
[li]Number of floors of
formwork equipment used.[/li]
[li]The building's structural system (e.g. flat plate, one-way or 2-way slab, beam & slabs, P/T, transfer floors or beams, etc.).[/li]
[li]Type & strength of posts used as reshores.[/li]
[li]Concrete placement procedure & sequence.[/li]
[/ul]
The applicable combination of the above factors for a specific structure then influences how one approaches the Reshoring (or Backshoring) analysis.
Note carefully ACI's definitions for Reshores & Backshores.
Analysis is kind of a 4-D problem as time (the continuing strength gain) becomes the 4th 'D'.
ACI 347 recommends a "Simplified Approach" which can be found in ACI-347.2R-05.
Link
I use a "translated" form of that method for my clients' structures, and have used it successfully for a few decades.
There really isn't one fits-all "Procedure" as the project-specific combination of the previously mentioned factors can dictate different methodology.
The over-riding concept: The applied construction load must be safely distributed (through the shores/reshores) to an appropriate combination of completed floors below at each stage of the construction cycle.
Ralph
Structures Consulting
Northeast USA