Hi All,
The G.C. has submitted an RFI stating that the anchors I specified, F1554 Gr.55,are not readily available and would delay the project schedule. He has asked to use F1554 Gr.36 but has also submitted a mill test report showing that the Gr. 36 A.R he is proposing exceed the properties of Gr. 55. The mill report show: Yield Strength = 57.2 KSI, Tensile Strength = 75.1 KSI, Elongation Test = 45%.
I think my options are (1) go through my calcs and re-run my governing cases to see if Gr.36 KSI works (I'm pretty sure it won't) (2) Accept his mill test since it meets my original design assumption of Fy=55 KSI and Ft=75 KSI. (3) Tell him to find the correct anchor rods.
Any input is appreciated and thank you all in advance.
The G.C. has submitted an RFI stating that the anchors I specified, F1554 Gr.55,are not readily available and would delay the project schedule. He has asked to use F1554 Gr.36 but has also submitted a mill test report showing that the Gr. 36 A.R he is proposing exceed the properties of Gr. 55. The mill report show: Yield Strength = 57.2 KSI, Tensile Strength = 75.1 KSI, Elongation Test = 45%.
I think my options are (1) go through my calcs and re-run my governing cases to see if Gr.36 KSI works (I'm pretty sure it won't) (2) Accept his mill test since it meets my original design assumption of Fy=55 KSI and Ft=75 KSI. (3) Tell him to find the correct anchor rods.