GE Steam Turbine Control Valve Not opening 1

Status
Not open for further replies.

TurbMaintEng

Mechanical
Nov 9, 2009
5
0
0
US
Got one for you to ponder:


We have an issue on U1. The MHC system/control valves are setup such that CV’s 1/2/4 have the same cam profile & timing and therefore all move together. CV3 has a different cam profile and is the last to open/first to close. The unit starts in full arc mode on the SVBV’s. U1 was operating normally on 5/21 and removed from service due to a boiler tube leak (controlled shutdown). The subsequent restart was on 5/26. When reset, all 4 CV’s went 100% open. When control was transferred to the governor/CV’s the behavior was as expected, CV’s 1/2/4 closed to approximately 13 -14% open, then increased to about 22% open and controlled the load while CV3 went to 0% open. The load at that point was about 40 mw. Load was then increased to about 170 mw with little to no change in CV position for any of the 4 valves. This is typical startup behavior, the load increase is due to main steam pressure being increased from about 900 psig to 3500 psig. At 170 mw the unit tripped due to a controls issue on the boiler side. The controls issue was addressed and the unit restarted about 6 hrs later. Again, on reset all 4 CV’s went to the 100% open position. When the valve transfer occurred, CV’s 1/2/4 all closed down to about 13 – 14% open and then increased to about 20 -22% to control load. Startup followed the normal path up to about 190 mw. At that point, the governor camshaft position increased and began increasing the lift for the CV’s 1/2/4. CV’s 2 &4 followed camshaft position normally and opened as camshaft position increased. CV1 however, never moved from 22%. Load was increased to 375 mw. CV’s 2&4 were approximately 32% open but CV1 was still at 22%. Load eventually was increased to 780 mw. CV’s 2&4 were at 100%, CV3 was at 45% and CV1 was still at 22%. Over the past couple days the load has been up and down between 780 and 375. Everything looks normal with the exceptions of CV1 & CV3. CV1 has never moved from 22% and CV3 opens further at high load (which makes sense, the governor cam shaft is a couple percent higher at full load which drives CV3 open more, and that is happening because CV1 is not 100% open like is should be). 10 days ago, at 780 mw, with CV’s 1/2/4 at 100% open, CV3 was at about 33% open. So, now we are seeing it run about 12% further open to achieve the same generation (and presumably the same steam flow rate).



It seems strange to me that this would be a case of mechanical binding (stuck valve) because it stroked to 100% open on the startup just 3 days ago? I looked externally and don’t see obvious issues with linkage, etc. Our control oil pressure indication shows that it is normal. At 375 mw (our normal low load bottom end), the camshaft position still calls for CV’s 1/2/4 to be above 22% open so I can’t say whether the valve will move in the closed direction or not. Although, on startup it did move from 100% open to 13% during the valve transfer. Could we have a linkage issue on the CV1 servomotor or pilot valve that would explain this? Oil leakage on pilot valve or operating cylinder that crossed a threshold point coincidently at the same time as valve transfer on startup and now we don’t have enough hydraulic pressure for CV1 servo?



Any thoughts?



The plan as of now is keep U1 in-service and perform the mini on U2. After that, we will have to make a decision because I don’t believe we can run a successful PJM capacity verification test on U1 with CV1 only 22% open. Looking for some ideas on what the scope of work would be to troubleshoot/address this issue and return unit to service (assuming that we have to shutdown and get into the servo enclosure at a minimum).

 
Replies continue below

Recommended for you

Seems like you'd get a lot of excess flow erosion on the single CV that is only open 22%.

I'd recommend NOT starting the second outage until you've at least fully resolved the reason the control valve on the first unit is not cycling properly and predictable.

You're betting the entire funding stream and reliability for both running control and shutdown control for the plant (when U1 is running while U2 is shutdown) on the single CV control valve that you know isn't working.

What does your GE testing rep say? Our practice is not to "release the outage report" (turn over the plant after an outage) until the customer accepts the test results for control and excitation.
 