mmxx

Mechanical
Mar 2, 2022
2
0
0
AU
Looking for correct procedure for grounding T2 and t3 joined(240v) on single phase 240v generator in AU with T1- L1 HOT, T4 -L2 neutral ,using Onan 12.k5va 4 wire ,being used in an agricultural environment any help much appreciated
 
Replies continue below

Recommended for you

Onan has made many different models in that size range over the years. If you have the specific model, spec and serial numbers of the subject generator, I may be able to help.
 
Hi Wayne have sorted it out Being stand alone in AU,with no power from grid ,with 2 wire 240v only 240 across active and neutral i just ground green with earth stake thankyou
 