electrageek
- Mar 11, 2002
- 116
We have a 30 year old GE 20MW 13.8kV generator runinng at 10MW with a Power Factor or 1.0. The field is rated at 250VDC at 199Adc maximum. The excitation is provided by a Basler Static Full wave unit. We run at approximately 90Vdc at 100Adc most of the time. We consistently have arcing on the outside collector rings. It is not there all the time it seems to come and got but it is generally related to the amount of field current. There is never any arcing on the inside rings.
We have tried:
1. Comparing the hardness between the inside and outside rings. They are the same.
2. Increase the brush pressure with new brush holders.
3. There is no vibration or out of roundness.
4. Swapped the polarity of the power going to the rings.
5. Checked and reworked the connection from each embeded copper cable coming from each brush to the ring.
6. Cleaned and resurfaced the ring to remove the pitting.
I am now thinking it might be a metallurgy problem. Something has happened to the outside ring metal that has increased it's resistance. The photo I attached shows an interesting thing. It almost appears that there is a pitted area about the shape of the brush itself. Could it be an pulsation from the excitation system happening at the same time each revolution? But why only on the outside ring?
I am looking for some new ideas and possible tests to run.
We have tried: