Hellow experts
I will appreciate any suggestion regarding this issue.
a generator 11kv 5.5 kw rated current 361 A.
the generator tripped 87 Diff protection. while sharing the load with the other units.
check the CT's all good and IR test was good. cleaning the lugs and start the generator but it tripped on 87 Diff again after 2 weeks.
found the DE Vibration probe wire burn out also the RTD module, seems to be result for high leakage current.
IR test 10 kv 1 mins.:
phaseA 27Gohm ,phaseB 21Gohm and phaseC 4Gohm.
High pot test:
phase A 29 kv, leakage current was 30 micro ampere
phase B 29 kv, leakage current was 20 micro ampere
phase C 22 kv, leakage current was 250 micro ampere (phase C break down after 22KV)
high pot test for phase C not good, CT ratio 500/5 Pick up current 0.2 in the protection relay,
so the required cuurent to energize 87 protecion = 0.2 *361/CT ratio = 0.722 A. the leakage current still in micro ampere and IR test still good why the diff. energized ?
based on the previous tests,is the generator can be repaired on site or not? what is repairing required?
regards
I will appreciate any suggestion regarding this issue.
a generator 11kv 5.5 kw rated current 361 A.
the generator tripped 87 Diff protection. while sharing the load with the other units.
check the CT's all good and IR test was good. cleaning the lugs and start the generator but it tripped on 87 Diff again after 2 weeks.
found the DE Vibration probe wire burn out also the RTD module, seems to be result for high leakage current.
IR test 10 kv 1 mins.:
phaseA 27Gohm ,phaseB 21Gohm and phaseC 4Gohm.
High pot test:
phase A 29 kv, leakage current was 30 micro ampere
phase B 29 kv, leakage current was 20 micro ampere
phase C 22 kv, leakage current was 250 micro ampere (phase C break down after 22KV)
high pot test for phase C not good, CT ratio 500/5 Pick up current 0.2 in the protection relay,
so the required cuurent to energize 87 protecion = 0.2 *361/CT ratio = 0.722 A. the leakage current still in micro ampere and IR test still good why the diff. energized ?
based on the previous tests,is the generator can be repaired on site or not? what is repairing required?
regards