My experience is similar to Bill's, differential can be applied but may not protect from all faults. Likely if this is a "packaged" genset it uses the generator control panel to provide electrical protections which are usually pretty basic), along with the start and stop controls. A unit of that size that I get a round most tends to be very "cost sensitive", meaning no one really wants to spend anymore than they absolutely have to most times.
Your application, such as standby, prime or parallel to grid all have a possible impact on how any protection will function and what really is required.
Modern multi-function relays, like an SEL 700G could go a long way in providing very good protections for your generator, but depends on how the generator is installed, grounded and who develops and implements the protection scheme.
If you provided some additional details you may get some better answers, likely your best solution is to hire a local engineer that has experience in generator protection and local codes/regulations.
Here is a link to a paper by Beckwith regarding generator protection,
Basler also has some good papers on the subject but their new website sure makes it hard to find
And depending where in the world you are there may be others, but I'm assuming US or somewhere close based on your voltage and rating
Hope that helps, MikeL.