Good evening ,
please let me tell you a story about two gensets of 3 generators each:
the first one is powered by 4045HF150 John Deere engines , with Stamford UC224D alternators. rated to 110 KVA standby.we can call it George.
the second one , powered by John Deere 4045HF150 and fitted with Stamford UC224D alternators , is rated to 140 KVA standby.lets call him Lennie.
george is installed in a small hospital , with almost no load, and is quite happy.
Lennie is supplying power to a much more busy hospital , and is acting weird: when load reach 50% , the engine start to lose frequency and shutdown ,the load sharing system start another engine and Georges gets crazy , with a loop of under frequency on the 3 engines of the genset and final shutdown of the entire genset.oups.
Okay , lets check the programming of PLC , cooling system , fuel system , injection pumps , wiring ad so on. all is good. damned !
lets look at the specs of the engines and alternators.
well it occurs that , according to the manufacturer , the UC224D alternator has a rating of ...63 KVA.
an intresting thing is that Lennie has a name plate on each alternators , apparently homemade , who stipulate that the prime power is 142 KVA...
the John Deere database ( is very good , i found that George and Lennie engines have the same specifications and were manufactured at the same date , in the same factory.
do you guys have already seen such a thing ? relabeling an alternator to a higher power ?
Best regards
Jean Michel
please let me tell you a story about two gensets of 3 generators each:
the first one is powered by 4045HF150 John Deere engines , with Stamford UC224D alternators. rated to 110 KVA standby.we can call it George.
the second one , powered by John Deere 4045HF150 and fitted with Stamford UC224D alternators , is rated to 140 KVA standby.lets call him Lennie.
george is installed in a small hospital , with almost no load, and is quite happy.
Lennie is supplying power to a much more busy hospital , and is acting weird: when load reach 50% , the engine start to lose frequency and shutdown ,the load sharing system start another engine and Georges gets crazy , with a loop of under frequency on the 3 engines of the genset and final shutdown of the entire genset.oups.
Okay , lets check the programming of PLC , cooling system , fuel system , injection pumps , wiring ad so on. all is good. damned !
lets look at the specs of the engines and alternators.
well it occurs that , according to the manufacturer , the UC224D alternator has a rating of ...63 KVA.
an intresting thing is that Lennie has a name plate on each alternators , apparently homemade , who stipulate that the prime power is 142 KVA...
the John Deere database ( is very good , i found that George and Lennie engines have the same specifications and were manufactured at the same date , in the same factory.
do you guys have already seen such a thing ? relabeling an alternator to a higher power ?
Best regards
Jean Michel