We have five horizontal, 3.3 MW each, air-cooled hydroelectric generators. Generator 2 has started to trip on high stator winding temperature, while running at full load. Its worth mentioning that this generator was rewound (not by the original manufacturer) a couple of years because its was damaged due to a fire incident. My questions are:
1- would the generator capability curves change after rewinding the generator?
2- is it possible that the unit got derated after rewinding?
3- I want to measure the resistance of the stator RTDs for calculating the temperature of the winding and also at the same measuring the actual stator winding temperature with an infra red heat sensor. This is to ascertain that the RTDs are functioning properly. If I disconnect the RTDs would it trip the generator? Because I think the protection system would see a very high resistance i.e. the open terminals of the RTD.
4- any further suggestions?
1- would the generator capability curves change after rewinding the generator?
2- is it possible that the unit got derated after rewinding?
3- I want to measure the resistance of the stator RTDs for calculating the temperature of the winding and also at the same measuring the actual stator winding temperature with an infra red heat sensor. This is to ascertain that the RTDs are functioning properly. If I disconnect the RTDs would it trip the generator? Because I think the protection system would see a very high resistance i.e. the open terminals of the RTD.