Based on a thread from last week in which the use of proprietary wood fasteners was brought up, I decided to take a deeper look into GRK RSS screws. I've noticed in the past large differences between manufacturer data and the lateral design values found in NDS Tables 12J and 12L for lag/wood screws.
Based on test data from ICC-ES Evaluation Report ESR-2442, Table 3, I created my own new table (see attachment) comparing the test data to values calculated per NDS 2018, Section 12.3. With a few exceptions, the test data indicates greater fastener strength than predicted by NDS. This isn't surprising, but the difference between the values in many cases is more significant than I would expect. In most cases tested values are at least 50 percent greater than NDS values. Several values are 2 or 3 times greater.
I'm curious if other engineers use this test data considering the huge difference compared to the NDS values in some cases. For a 5/16"x6" RSS PHEinox fastener, for instance, with perpendicular to grain loading (ledger type connection), it seems like you could used half or less screws versus standard screws calculated per NDS. (I suppose that's their whole selling point!)
The following are a few potential risks that I can think of with using the test values:
[ol 1]
[li]If the builder does not use the specific proprietary fastener called for and the substitute does not have similar test data, then the number of fasteners required could be significantly more, and the connection will likely not pass.[/li]
[li]If a connection were to fail and it was found that the field conditions did not exactly match the test conditions. For example, a 5/16" RSS fastener has test data for side member thicknesses of 1.5" and 2". If the side member were really 1.75", could an intermediate value be interpolated? Engineering judgement of course says yes, but if there was a problem that resulted in litigation, how would this hold up in court?[/li]
[li]What if a future evaluation report indicates that previous test values were too high? I assume that the evaluation report is an extension of the building code and that the engineer would not be liable for any errors, although I don't know.[/li]
[/ol]
I realize that I'm probably being overly cautious with some of this, but it seems a little crazy that we can suddenly use significantly less fasteners in most connections. Any comments are appreciated.
Based on test data from ICC-ES Evaluation Report ESR-2442, Table 3, I created my own new table (see attachment) comparing the test data to values calculated per NDS 2018, Section 12.3. With a few exceptions, the test data indicates greater fastener strength than predicted by NDS. This isn't surprising, but the difference between the values in many cases is more significant than I would expect. In most cases tested values are at least 50 percent greater than NDS values. Several values are 2 or 3 times greater.
I'm curious if other engineers use this test data considering the huge difference compared to the NDS values in some cases. For a 5/16"x6" RSS PHEinox fastener, for instance, with perpendicular to grain loading (ledger type connection), it seems like you could used half or less screws versus standard screws calculated per NDS. (I suppose that's their whole selling point!)
The following are a few potential risks that I can think of with using the test values:
[ol 1]
[li]If the builder does not use the specific proprietary fastener called for and the substitute does not have similar test data, then the number of fasteners required could be significantly more, and the connection will likely not pass.[/li]
[li]If a connection were to fail and it was found that the field conditions did not exactly match the test conditions. For example, a 5/16" RSS fastener has test data for side member thicknesses of 1.5" and 2". If the side member were really 1.75", could an intermediate value be interpolated? Engineering judgement of course says yes, but if there was a problem that resulted in litigation, how would this hold up in court?[/li]
[li]What if a future evaluation report indicates that previous test values were too high? I assume that the evaluation report is an extension of the building code and that the engineer would not be liable for any errors, although I don't know.[/li]
[/ol]
I realize that I'm probably being overly cautious with some of this, but it seems a little crazy that we can suddenly use significantly less fasteners in most connections. Any comments are appreciated.