Tesla1971
Electrical
- Feb 13, 2003
- 6
My question pertains to the codes for the United States, namely the NEC.
I currently have a project where I need to accomplish the following:
Generator - AC Distribution Panel - Load 1 / Load 2 / Load 3
Basically I am employing a 200kW, 600V, 3-phase, 4-Wire Generator in a substation for "essential power".
The Generator will be located in the middle of the substation. It will be connected directly to a 400A, 600V, 3-phase AC Distribution Panel with Main Breaker of 250Amps (about 10 feet away). The AC Panel will also have 3 Feeder Breakers that will connect to 3 Station Service Transformers located throughout substation (between 800-1200 feet away).
The Station Service Transformers will be step-down transformers: 600V-208/120V.
Since I would only need the L-L voltage of 600V (as opposed to the L-N voltage of 346V), I would like to know if I would have to pull a ground wire from the AC distribution Panel to each of the Station Service Transformers?
Or would I only need to pull the 3-conductors for each phase and simply ground everything (generator, AC Panel, Station Service Transformer) individually to the ground grid.
I currently have a project where I need to accomplish the following:
Generator - AC Distribution Panel - Load 1 / Load 2 / Load 3
Basically I am employing a 200kW, 600V, 3-phase, 4-Wire Generator in a substation for "essential power".
The Generator will be located in the middle of the substation. It will be connected directly to a 400A, 600V, 3-phase AC Distribution Panel with Main Breaker of 250Amps (about 10 feet away). The AC Panel will also have 3 Feeder Breakers that will connect to 3 Station Service Transformers located throughout substation (between 800-1200 feet away).
The Station Service Transformers will be step-down transformers: 600V-208/120V.
Since I would only need the L-L voltage of 600V (as opposed to the L-N voltage of 346V), I would like to know if I would have to pull a ground wire from the AC distribution Panel to each of the Station Service Transformers?
Or would I only need to pull the 3-conductors for each phase and simply ground everything (generator, AC Panel, Station Service Transformer) individually to the ground grid.