We have experienced a strange problem at a new installation:
We have a 3-wire ATS fed from a 3-wire grounded 3-wire 480-volt service, as well as a 3-wire grounded emergency generator source. ATS is reported to have midpoint-off position, although delay setting is unknown (currently being verified). ATS loads are (4) 3-wire elevators.
As part of comissioning, the generator was manually started, and a manual transfer to emergency was initiated. The emergency breaker tripped on ground fault, the ATS automatically retransferred to utility, and utility then also tripped on ground fault.
The breakers were reset and power was restored with no other corrective action. Feeders insulation had previously tested OK.
We have not been able to recreate the problem since, transfers have been OK. However, a concern remains about future failures of the emergency power system.
Some possible explanations come to mind:
1) Intermittent motor fault
2) Intermittent feeder fault
3) Super-low setpoints on ground fault pickup (or sensor) -- we're currently checking this.
4) Bad filter or TVSS in elevator controller
These two would seem to be easy enough to test for -- any specific recommendations on specific tests?
Here's some other explanations, although they all seem less probable:
5) Harmonics -- but zero-sequence current harmonics are not possible with 3-wire system, are they?
6) Insufficient mid-point delay on ATS -- but that would only show up as an overcurrent, not as a ground fault, right?
Any thoughts on this? Any of the above that we can eliminate as impossible? Any other potential problems I might have overlooked?
We have a 3-wire ATS fed from a 3-wire grounded 3-wire 480-volt service, as well as a 3-wire grounded emergency generator source. ATS is reported to have midpoint-off position, although delay setting is unknown (currently being verified). ATS loads are (4) 3-wire elevators.
As part of comissioning, the generator was manually started, and a manual transfer to emergency was initiated. The emergency breaker tripped on ground fault, the ATS automatically retransferred to utility, and utility then also tripped on ground fault.
The breakers were reset and power was restored with no other corrective action. Feeders insulation had previously tested OK.
We have not been able to recreate the problem since, transfers have been OK. However, a concern remains about future failures of the emergency power system.
Some possible explanations come to mind:
1) Intermittent motor fault
2) Intermittent feeder fault
3) Super-low setpoints on ground fault pickup (or sensor) -- we're currently checking this.
4) Bad filter or TVSS in elevator controller
These two would seem to be easy enough to test for -- any specific recommendations on specific tests?
Here's some other explanations, although they all seem less probable:
5) Harmonics -- but zero-sequence current harmonics are not possible with 3-wire system, are they?
6) Insufficient mid-point delay on ATS -- but that would only show up as an overcurrent, not as a ground fault, right?
Any thoughts on this? Any of the above that we can eliminate as impossible? Any other potential problems I might have overlooked?