Heldbaum
Civil/Environmental
- Jan 27, 2017
- 128
Hi everyone, I need to provide shop drawing and design for 2' high "H-Way Rail" in the garage as per attached plan view and other info. This is a garage of a residential building. They call it a H-Way Rail and it will sit on a 6" high by 8" wide curbe. When I realized that I have to apply 6,000 lbs horizontal load at 2' above garage floor (as per NYC BC) (unless I don'?)I decided to anchor the post, which for now is HSS 4x4x3/8, to the concrete slab and they will build the curb around the posts (the curb is not there yet). But still I am having a hard time to design epoxy anchors for that moment from 6 kips horizontal load and shear force. Please look at the attached when you have a minute. Anyone has any experience with something silimiar and would like to share ? NYC BC says 6,000 lbs 2' and 3" above the slab elevations which in my case is almost at the top of the post..that gives 19 kip-ft LRFD moment and 9.6 kips shear. Even when I multiply by say 0.8 to account for load being shared between posts it is still a lot. I asked EOR for load criteria so he pointed me to the building code..
What if I do not rely only on anchors but also on that 6" high curb that will be built ? Can I assume that part of that moment will be "taken" by the curb ? If so how would you solve it? All thoughts much appreciated. Thank you in advance.
What if I do not rely only on anchors but also on that 6" high curb that will be built ? Can I assume that part of that moment will be "taken" by the curb ? If so how would you solve it? All thoughts much appreciated. Thank you in advance.