I feel like I am missing something. I have run the calculations on a 3'-6" tall handrail post several times in this delusional hope that the calculations will come out differently but sure enough, they don't. The calcs point to needing a 1-1/2" STD handrail post (which has an O.D. of 1.9") to sustain the required load (50 lb/ft or a 200 lb concentrated load). But time and time again I check stair shop drawings where they call out a 1-1/4 STD pipe. Which, I have checked and absolutely does not work. I assume they do this so they can get away with a smaller stringer size (a MC12x10.6 as opposed to the C12x20.7 which has a larger flange width to accommodate the larger pipe), But I really don't know. Does anyone have any insight into this as to any other reasons why stair manufacturers use these smaller handrail posts ALL the time??