Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

harmonics noise advisement

Status
Not open for further replies.

vetlover

Electrical
May 4, 2005
12
Need to see if someone can suggest a person or organization that can take a look at charting from hioki power analyzer that may make suggestions as to a solution for problem. DC plating process is interfering with upstream AC equipment.
 
Replies continue below

Recommended for you

Does it really interfere? Or has someone taken a recording and got worried for no reason at all?

Usually, harmonics do not cause much trouble - unless you have PF capacitors than can resonance with the harmonics. I can have a look at the recordings. Try to isolate address from this: "edmatgkeorg". A dot is needed before org. The rest is a no-brainer.

Gunnar Englund
 
Gunnar,
Thanks for your response, I should have readings by Wed. evening and will send to you then. I will explain situation more in detail at that time.
Vetlover
 
Gunnar,
I have sent drawings-Thursday afternoon. Thanks for your view. Vetlover
 