Maddog:
I have looked at VFD's (VDS's) for capacity control for the systems I build, and don't think it is a good idea. First of all, I think VFD's are great, if applied properly. Unfortunately, it adds a degree of cost and complexity to a residential A/C system that is not justified by the benefits. In addition, there are other technologies that are better suited.
Here are some negatives:
1. Compressors manufactures are really sensistive to you putting anything but line voltage to the compressor. They get real antsy whenit comes down to a warranty situtation.
2. Lubrication- The demand for oil doesn't necessarily decrease proportionally with a decrease in speed. Most res. A/C systems have hermetic compressors and no auxiliary oil pumping system. Your car can't run without oil, nor can a compressor.
3. Scroll compressor technology is overtaking res. A/C. Many are Copeland Compliant scroll. I can't speak for other mfg's, but the compliant sroll uses the centrifugal force of the orbital scroll to maintain the seal to the fixed scroll. If you slow down too much, you lose the seal, and don't pump. This may actually work as an unloading strategy, but is probably not endorsed by Copeland.
4. Some manufacturers (Manuerop/Danfoss) use scrolls with tip seals, and have reciprocatiing compressors that are packaged with VFD's. THe recips are small, and they don't recommend running at less than 40 Hz. I'm not sure that modulating between 40-60 Hz would really add much benefit versus the cost.
5. Someone made a post on that above link about using an external "prime mover;" an open drive compressor. I don't think they currently exist less than 50 HP (For R-22). They would be so much more expensive that it wouldn't be feasible for residential AC even if they made them in the 3-5HP range. Plus the seals leak if not properly maintained. What homeowener will take care of that properly? I probably wouldn't.
If you go to
they have some articles about their scroll compressors with built in unloading. They also have a thing called a digital scroll wich unloads the compressor by axially unloading the scrolls (due to the compliance feature I mentioned above). It can modulate faster than a VFD because you don't have to worry about the inertia of the rotor and compressor.
I don't want to be a Luddite. VFD's have many applications in A/C (controlling fan speed to maintain head pressure, works great), varying the rate of chilled water to fan coils, etc.
In short, great concept but in reality, the costs outweigh the benefits.
Clyde the Mule
P.S.- I don't work for Copeland, I just use a ton of their compressors.