RandomUserName
Mechanical
- Apr 11, 2014
- 62
The following section is directly from the Trane SCWG Brochure (Unitary Vertical Self-Contained System). This is their example selection procedure:
--------------------------------------------
Design Conditions
Total gross capacity required = 368.7 MBh = 31 Tons
Total sensible capacity required = 259 MBh
Entering air temperature = 80/67°F
Entering water temperature = 85
gpm = 105
Selection Procedure
Airflow = 14200 cfm at 2.5-inch duct static pressure
Unit to include:
Constant Volume
Waterside economizer
Medium velocity throwaway filters
Unit Selection
Tentatively select a 35 ton unit. Refer to Table 13, p. 36 to obtain gross total and sensible unit
capacities, and gpm at the design conditions:
Total capacity = 370 MBh
Sensible capacity = 282 MBh
LWT = 95.4°F
Since the design cfm is greater than the nominal cfm, adjust the capacities and condenser water
delta T to reflect the higher cfm:
design cfm/nominal cfm 14,240/14,000 + 3% from nom. Cfm
Refer to Table 6, p. 29 to obtain the capacity correction factors for +3% of nominal cfm:
Cooling capacity multiplier = 1.005
Sensible capacity multiplier = 1.014
Multiply the capacities by the correction factors:
370 MBh x 1.005 = 371.85 MBh
282 MBh x 1.014 = 285.95 MBh
The SCWG 35 meets the total and sensible design requirements.
--------------------------------------------
I am not understanding the logic here I was hoping those with more experience than me could teach. See items in bold above. Their unit selection is for Qt = 368.7 MBh and Qs = 259 MBh. I would assume this means they have a latent load of Ql = 368.7 - 259 = 109.7 Mbh they need the coil to remove.
Their final unit selection has numbers of Qt = 371.85 MBh and Qs = 285.95 MBh. This would mean the coil can only condense Ql = 85.9 MBh out of the airstream.
Is this not a bad selection? I would think they would have humidity issues if the latent load was not met. I am under the impression that in this case, you would either reduce the fan speed if possible - making sure you are still meeting your sensible load and OA requirement - or "bump up" to the next size unit - in this case from 35 ton to 40 ton - to get your latent load.
Could you guys help a young engineer understand the logic here?
Thanks!
--------------------------------------------
Design Conditions
Total gross capacity required = 368.7 MBh = 31 Tons
Total sensible capacity required = 259 MBh
Entering air temperature = 80/67°F
Entering water temperature = 85
gpm = 105
Selection Procedure
Airflow = 14200 cfm at 2.5-inch duct static pressure
Unit to include:
Constant Volume
Waterside economizer
Medium velocity throwaway filters
Unit Selection
Tentatively select a 35 ton unit. Refer to Table 13, p. 36 to obtain gross total and sensible unit
capacities, and gpm at the design conditions:
Total capacity = 370 MBh
Sensible capacity = 282 MBh
LWT = 95.4°F
Since the design cfm is greater than the nominal cfm, adjust the capacities and condenser water
delta T to reflect the higher cfm:
design cfm/nominal cfm 14,240/14,000 + 3% from nom. Cfm
Refer to Table 6, p. 29 to obtain the capacity correction factors for +3% of nominal cfm:
Cooling capacity multiplier = 1.005
Sensible capacity multiplier = 1.014
Multiply the capacities by the correction factors:
370 MBh x 1.005 = 371.85 MBh
282 MBh x 1.014 = 285.95 MBh
The SCWG 35 meets the total and sensible design requirements.
--------------------------------------------
I am not understanding the logic here I was hoping those with more experience than me could teach. See items in bold above. Their unit selection is for Qt = 368.7 MBh and Qs = 259 MBh. I would assume this means they have a latent load of Ql = 368.7 - 259 = 109.7 Mbh they need the coil to remove.
Their final unit selection has numbers of Qt = 371.85 MBh and Qs = 285.95 MBh. This would mean the coil can only condense Ql = 85.9 MBh out of the airstream.
Is this not a bad selection? I would think they would have humidity issues if the latent load was not met. I am under the impression that in this case, you would either reduce the fan speed if possible - making sure you are still meeting your sensible load and OA requirement - or "bump up" to the next size unit - in this case from 35 ton to 40 ton - to get your latent load.
Could you guys help a young engineer understand the logic here?
Thanks!