Here is a related former thread that I couldn't extract a clear answer from:
Here's a link to illustrate my question:
On the left is a headed stud that we can say is governed by concrete tension breakout. On the right is a deformed rebar with an embedded length equal to ld per 25.4.2.3 of ACI 318-14.
Let's say I wanted to design an anchor for a wall. Why would I ever use headed studs if I can use rebar to get WAY more strength in tension. Furthermore, in thinner slabs, the edge distance effects kill the capacity of headed studs in tension. Meanwhile, the embedded deformed bar could maintain huge capacities even at very small edge distance (cb value in the ACI equation). This logic seemed crazy, so I reached out to a manufacturer that uses embedded rebar tails and under tension loading the capacity is based on concrete breakout (determined by testing).
So now my understanding is the development length formula for deformed bars is only valid to prove the full capacity of the rebar can be transferred into the concrete (ie. bond). But a separate check would still be required to determine if the local area of the concrete can handle the load imposed upon it by the rebar. I think using the checks for an adhesive anchor make more sense for embedded deformed bars, but due to lack of knowledge I'd probably take the worst case between headed stud and adhesive. Thoughts?
Here's a link to illustrate my question:
On the left is a headed stud that we can say is governed by concrete tension breakout. On the right is a deformed rebar with an embedded length equal to ld per 25.4.2.3 of ACI 318-14.
Let's say I wanted to design an anchor for a wall. Why would I ever use headed studs if I can use rebar to get WAY more strength in tension. Furthermore, in thinner slabs, the edge distance effects kill the capacity of headed studs in tension. Meanwhile, the embedded deformed bar could maintain huge capacities even at very small edge distance (cb value in the ACI equation). This logic seemed crazy, so I reached out to a manufacturer that uses embedded rebar tails and under tension loading the capacity is based on concrete breakout (determined by testing).
So now my understanding is the development length formula for deformed bars is only valid to prove the full capacity of the rebar can be transferred into the concrete (ie. bond). But a separate check would still be required to determine if the local area of the concrete can handle the load imposed upon it by the rebar. I think using the checks for an adhesive anchor make more sense for embedded deformed bars, but due to lack of knowledge I'd probably take the worst case between headed stud and adhesive. Thoughts?