Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Heat exchanger flow rate 1

Status
Not open for further replies.

RS82

Mechanical
Mar 5, 2012
35
Hello, could you someone explain to me the effect of increasing the process fluid flow rate, in the tube, in regards to the heat transfer to the cooling water in the shell?

What happens if I increase or decrease the flow rate in the tube by keeping the cooling water flow rate constant?

What happens if the cooling water flow rate in increased or decreased with the process fluid flow rate constant?

I was reading a heat exchanger chart which shows the outlet temperature with respect to the process fluid flow rate..it showed the inlet temp as 500F and with a flow rate of 2GPM, the fluid cooled down to 300F..and with 1GPM it went from 500F to 200F..by increasing the process fluid flow rate, is the heat transfer rate reduced?
 
Replies continue below

Recommended for you

Q = U A [Δ]T[sub]LM[/sub] = w C[sub]P[/sub] [Δ]t

Then you have two choices. U is constant or U changes with the flow rate.

Sounds very textbookish to me.

Good luck,
Latexman
 
"it showed the inlet temp as 500F and with a flow rate of 2GPM, the fluid cooled down to 300F..and with 1GPM it went from 500F to 200F..by increasing the process fluid flow rate, is the heat transfer rate reduced? "

Really? How did you come to that conclusion? Perhaps you're just being sloppy with terminology. Since you say nothing about your cold side, I'll assume that nothing changed. If nothing changed, then the transfer RATE is constant. What's changed on the hot side is that you decreased the POWER = Joule heat*flow rate. Decreased power results in a larger temperature drop

TTFN
faq731-376
7ofakss
 
RS82,
changing the process fluid flow rate will change its exit temperatures.

the overall heat transfer coefficient is dependent on both the cooling water and process water flow rates since it is a function of the convection heat transfer on the shell side and tube side. Any heat transfer textbook will show u a basic understanding on how and why it depends on these flowrates.

when you change the process fluid flow rates, the amount of heat transferred from the cooling water to the process fluid does not change assuming that your inlet temperatures stay constant. What happens is that your U, exit temperatures and hence ΔTLM will adjust to match the "same" heat transferred.

On the other hand, your overall heat transfer area remains a constant.

 
Heat transfer is a function of the three "t's", time, temperature and turbulence. Velocity interacts with two of them in a major way and one in a lesser way.

Let's assume for a moment that the temperature rise of your cooling water is constant regardless of velocity - not true, but hold temperature for a moment.

Your Hx will have a "U" value at a given velociy with units expressed in heat units per unit of tube surface area per time unit - Btu's per hr per square foot per degF in English units. What is happening on each side of the tube will influence the "U" value. For now we are holding the process side constant. Therefore, if you increase the cooling water velocity to infinity, your fluid won't stay in the Hx long enough to absorb any heat. Obviously you wouldn't run it that fast, but that extreme is given to make a point.

On the other hand, as the velocity increases, (to a point) the turbulence increases, so you get better heat transfer at the higher reynolds numbers.

Now add the temperature back in because it is important to the conduction through the tube wall and the ovreall LMTD of the Hx. Slow the fluid down so much that it heats up to its exit temperature too soon and little to no heat transfer occurs in the last few feet/meters of the tube(s).

So it is a balancing act. Picking the velocity that will give you the best heat transfer for the surface area available.

rmw
 
Thanks folks..so if I would like to increase the heat transfer of the process fluid through the tubes, I should increase the flow rate to ensure it is turbulent flow..this way the exit temp will lower as opposed to slowing the flow rate down which creates a laminar flow which depends on the thermal conductivity of fluid..did I get this right?
 
Somewhat, the flow regime does not depend on thermal conductivity of fluid. What year in school are you? It appears you have not had fluid flow or heat transfer yet. Replies can accomodate students if we know. Otherwise, we assume you have at least a BS.

Good luck,
Latexman
 
From forum guidelines:

Academic related posts are discouraged. If you post topics related to undergraduate course-work or projects, your posts will be red flagged and marked for deletion. Students generally have vast resources available to them (libraries, professors, etc), and need to learn how to use those sources instead of relying on the Eng-Tips.com fora (it is similar to having someone else do your homework for you; not a good idea.)
 
"when you change the process fluid flow rates, the amount of heat transferred from the cooling water to the process fluid does not change assuming that your inlet temperatures stay constant. What happens is that your U, exit temperatures and hence ΔTLM will adjust to match the "same" heat transferred."

By what magic do you get this??
 

On the process fluid side:

Before: Q[sub]1[/sub] = w[sub]1[/sub]Cp[sub]1[/sub]ΔT[sub]1[/sub]
After: Q[sub]2[/sub] = w[sub]2[/sub]Cp[sub]2[/sub]ΔT[sub]2[/sub]

Now replacing the symbols with numbers one gets the following:

Q[sub]1[/sub] = (2×200) Cp[sub]1[/sub]
Q[sub]2[/sub] = (1×300) Cp[sub]2[/sub]

Assuming Cp[sub]1[/sub] ≈ Cp[sub]2[/sub] → Q[sub]1[/sub] = (400/300) Q[sub]2[/sub]

Then, to understand what happened, see Latexman's answer, for the overall equation.

Q = U×A×LMTD​

By keeping A constant and changing the others, since Q dimished, it means U×LMTD decreased.


 
Status
Not open for further replies.

Part and Inventory Search

Sponsor