Hello, Am new in the sprinkler s
angie
GH
Am new in the sprinkler system/ hydrant design. am suppose to design a 6 hydrant system with a pump connected to a water supply.
Could you please help me with the type of pump to use,
the pump pressure calculation, the pump gpm and also the pump head.
First you have to determine the most demanding scenario. For example 2 hydrants working simultaneously. This demands (for example) 2x 1000 lpm at 3 bar. Then your pump according to NFPA has to be:
Flow-Rates
625 GPM
The working pressure depends on the length, diameter and friction of your pipe. If you expect (and you should calculate this) a pressure drop of 1 bar from pump to the hydrant, your pump should work at at least 4 bar.
Also you need to specify the type of water supply.
If there is positive pressure at the fire pump suction
you will normally use a centrifugal pump, either:
- horizontal split case
or
-vertical inline.
If you are lifting water from a pit or a pond you will need a turbine pump.
Thanks guys. The water pressure is 2bar and running through a pipe of pn10.the Clients want 6 hydrant at a distance of 200m each. How can i calculate the type of pump to use and the pressure most importantly. Thanks
Do you mean that the demanded water pressure at the hydrant is 2 bar?
What kind of hydrant? What is the demanded flow?
What is the pipe size?
What is the pipe material (for estimating the pressure loss due friction)?
The static pressure is 2bar. And its a wet barrel hydrant. The pipe size is a 4" hdpe pipe. PN 10 HDPE pipe. the water supply has a pressure of 2 bar and its the main waterline which the pump would be connected to.
