help for electricity distribution (HTA) through underground cables (6 circuits)

Status
Not open for further replies.

Ennajjar

Electrical
Jul 20, 2015
13
I'm studying Electrical engineering at faculty.I will be pleased If you can guide me and give me advices and directions to take for resolving some problems I meet during my internship.

Actually, I'm working on a project about a medium voltage electricity distribution (HTA) through underground cables. The first problem I met is concerning the induced current that flows in the cable screen; it is very high and causes the burning of cables and ends. the second problem is about the imported power, at the output we find it less than what is supposed to be posted.

I try to calculate the current following the IEC 60287 norm in each circuit for different mode. I need to know how can I calculate this current with the purpose to raise it by varying factors that impact on it. Also I don't know how can I use this norm for 6 circuits.

I will be very thankful If you can guide me and help me in my work.
Thanks in advance.

Mehdi Ennajjar
 
Replies continue below

Recommended for you

i can keep 500mm distance between conduits
 
The same formula, of course.
If you can keep only 500 mm distance between conduits [center line to center line] then 373 A will be the maximum [3*373=1119 A, 63.95 MVA[51.17 MW].
 
I need to have 30 MW for each duct and `i` must be equales to 584 to have p = 30MW !
how can I increase the power to 30 MW for each duct with reasonable divergence that not exceed 50 cm between ducts?
 
Sorry Ennajjar!
A group of 3 cables –only 3 single-core cables-each alone in a pvc conduit at 500 mm distance[3 conduits] withstands 600 A in the above mentioned conditions.
A group of 9 cables –three cables per duct- each cable withstands only 371 A.
A group of 6 conduits [18 single-core cables] 3 cable per conduit at 500 mm distance, each cable withstands only 300 A.

 