Hi-Pot Testing

Status
Not open for further replies.

Melco001

Electrical
May 30, 2008
15
What is the applied voltage test for a Hi-Pot testing on the lightning arrestors, CB´s, Disconect switches, etc. in a 115kV substation.
 
Replies continue below

Recommended for you

Is this an AC or DC HiPot test? For air break switches and circuit breakers we did an AC HiPot test to twice the rated line to line voltage. Check the manuals on the CB. They should have a HiPot value.

------------------------------------------------------------------------
If it is broken, fix it. If it isn't broken, I'll soon fix that.
 
Is it for DC power Hi-pot tester? 1.8 times 115KV. Thank you
 
Melco001,
that is the AC value. A test report with the CB should state the HP voltage. The manual should also state the DC, but I will get back to you.
 
Status