high P.I. (with good one-minute I.R.) 3

Status
Not open for further replies.

electricpete

Electrical
May 4, 2001
16,774
Can anyone provide information related to concerns that may be associated with the particular symptom of high Polarization Index P.I.?

For example, epoxy-mica medium voltage machine shows 20 G-ohms at one minute and 150 G-ohm at 10 minutes => PI = 150/20~7.5.
I am familiar with IEEE43 guidance that PI loses significance above 5 G-ohms one minute, since readings above this based on lower current can have error, but still interested in exploring possible meanings of this symptom).

I have heard various places this could indicate dry / brittle / resin-depleted insulation (thumbrule PI > 6 suggests this condition).

My two biggest questions:
1 - Does this "thumbrule" apply only to older Asphaltic systems?
2 - What is the physical reason why insulation systems which are dry / brittle / resin-depleted might have high PI?
3 - Has anyone seen high PI associated with insulation problems (on machine with good 1-minute IR)
4 - Any references?


=====================================
(2B)+(2B)' ?
 