High-tertiary impedance design change from 12% to 26% 1

Status
Not open for further replies.

EddyPach

Electrical
Jan 9, 2002
28
Can somebody explain what would be the effect of changing the H-Y (high to tertiary) impedance in a 120/160/200 MVA, 260-144/25 kV, three phase autotransformer, from 12% (required) to 26% (per design). The H-X impedance is 5%.
Thanks for the info.
 
Replies continue below

Recommended for you

The question is not clear.Can you explain?What is meant by "required" and "designed"?Also indicate T-X impedance also on both cases.Hope H-Ximpedance remains the same.
 
A corp. requires a 120/160/200 MVA auto Xfr with H-X=5% and H-Y=21% requirements. However our engineering can only comply with the H-X at 5%, and only provide H-Y = 36% impedance instead of 21%. My questions is what can possibly change with our deviation? Does it matter if the tertiary is buried or if it is loaded? If so, why should that be?
 
If the tertiary is buried it will not matter at all ,but in a way better as the circulating current in tertiary will be reduced.But if it is aloaded tertiary ,regulation at tertiary terminals will be higher as the T arm of the circuit will have higher impedance.
 