Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Hood Support CMC 508.4 2

Status
Not open for further replies.

hawkaz

Structural
Oct 28, 2010
412
Does anyone have any commentary that explains why the California Mechanical Code (section 508.4) requires hood supports to be able to support an additional 800 lbs. beyond the hood weight? This is more than the hoods themselves in many cases.

Thanks in advance
 
Replies continue below

Recommended for you

When you say 'hood', in what context is this? I mean, what kind of a 'hood'?

John R. Baker, P.E. (ret)
Irvine, CA
Siemens PLM:

The secret of life is not finding someone to live with
It's finding someone you can't live without
 
In this particular case, it would be a type I restaurant kitchen exhaust hood
Thanks
 
"Welcome to the pantry, pal"

LOL

The problem with sloppy work is that the supply FAR EXCEEDS the demand
 
Thanks- I did see that section of the CMC code. I was hoping for some background as to why this load is so high.
John McClane probably tops out at around 200 lbs, so it would take 4 of him to reach this load.
 
That's remarkably arbitrary.

If you have ever participated in the development of a code or standard then that wouldn't surprise you.

The California Mechanical Code is "based on the Uniform Mechanical Code".

The same 800 pound requirement appears in the UMC as far back as the 2012 version. I couldn't find any earlier versions in 2 minutes of Googling.

Good luck tracing things back farther.

 
To cover things that are hung off the hood?
To cover grease buildup?
To cover maintenance personnel weight times a safety factor?
 
Thanks. Good idea to look up commentary on older copies of the UMC, but I could not find anything more on this either.
 
Hawkaz:
The 800lbs. also likely includes an EQ (earthquake) component which should/might be applied in any direction. Other mech. equip., like water heaters and storage tanks must be tied back to the structure for lateral EQ loads too. You should always read the code commentary. That’s often more meaningful for a good understanding of the intent and original thinking than the code verbiage itself.
 
Thanks Dhengr,
Are you aware of any code commentary for this? I was not able to find any. Looking for that commentary was the purpose of this post.

The way I read this, Ev (from ASCE7) is separate (and additive) from this load.

 
I was just googling and ran across the online version of the 2021 International Mechanical Code. I don't see an 800-lb requirement, but do see "And the possible weight of personnel working in or on the hood" in 507.2.4 and a similar statement in 507.3.2.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor