Same project I'm working on doing the PM. I came in after all of the rebar has been installed and the hooked length of the vertical #5 bars for the foundation walls are 6 inches. Code requires 12db which is 7.5 inches.
Foundation is as follows:
16" deep x 24" wide footing
36" tall x 6" wide stemwall - #5's vertical and horizontal at 12" o.c.
light framed construction on top
Are there any alternatives solutions other than removing the vertical bars and redoing them?