K. Adam
Petroleum
- Apr 22, 2022
- 11
Good day Gents,
We are using a thermal oil as heating source to heat up our HC products and Glycol system. A flash fire occurred while removing an insulation material to investigate source of smoke in the flange area. As part of investigation, oil sample was collected, analyzed and the result shows a reduction in the flashpoint of hot the oil (186 & original flashpoint was 215 - as per MSDS) whereas our normal operating temperature is 240 C. Thoroughly checks carried out to check possible of degradation / contamination in the oil but all parameters found to be normal.
Can you share with me your thought to figure out the possible other root cause of reduction in flashpoint and what could be the impact to continue running the system with the same status (operating temperature higher than flashpoint)? and also possible root cause of flash fire considering that an oil sweep observed in the flange area and coke formation found to be around he flange!
thanks
We are using a thermal oil as heating source to heat up our HC products and Glycol system. A flash fire occurred while removing an insulation material to investigate source of smoke in the flange area. As part of investigation, oil sample was collected, analyzed and the result shows a reduction in the flashpoint of hot the oil (186 & original flashpoint was 215 - as per MSDS) whereas our normal operating temperature is 240 C. Thoroughly checks carried out to check possible of degradation / contamination in the oil but all parameters found to be normal.
Can you share with me your thought to figure out the possible other root cause of reduction in flashpoint and what could be the impact to continue running the system with the same status (operating temperature higher than flashpoint)? and also possible root cause of flash fire considering that an oil sweep observed in the flange area and coke formation found to be around he flange!
thanks