polyphase
- Oct 18, 2001
- 9
The situation I have is a 24.94-kV four wire grounded system normally serving load through a 24.94/12.47-kV delta/wye stepdown. Both the 12.47-kV and the 24.94-kV are four wire grounded wye systems. There is a desire to reverse the flow and serve several customers on the 24.94-kV side from a source on the 12.47-kV side. The existing stepdown bank is rated 1500 KVA and consists of (3) 500 KVA single phase transformers on a platform. There will be no path for ground current on the 24.94-kV side, so a grounding bank is required. I know that ZigZag is a better type of connection for grounding, but a bank of (3) grounded wye/delta connected single phase transformers are planned. How do I calculate the size the grounding bank?