How to calculate recovery time for a house in cooling mode? 1

Status
Not open for further replies.

lchandna

Mechanical
Dec 10, 2008
4
Hi guyz,
I am totally new to this site and looks like its a great place to post questions regarding engineering.
Anyways I am trying to calculate the approximate time required to recover the house temperature when going from unoccupied to occupied mode in cooling cycle. Thanks.
 
Replies continue below

Recommended for you

First order approximation is:

V*Cp*dT/Qx

where

V is the volume of the space
Cp is the volumetric heat capacity of air
dT is the difference between unoccupied and desired temperature
Qx is the quasi-instantaneous excess capacity of your cooling system.
 
Hi MintJulep,
Thanks a lot for your reply, but can you please explain how can I find out the Cp and Qx? Thank you.
 
Cp you look up.

Qx is rather more difficult. You could get a reasonable feel for the system's cooling capacity from the compressor's performance curves. The excess capacity is the difference between that and the cooling load at the same conditions.
 
Thanks a lot MintJulep. I'll look into it.
 
stopwatch trumps a flux capcitor

Take the "V" out of HVAC and you are left with a HAC(k) job.
 