Jimmyvanskip
Mechanical
- Apr 21, 2012
- 5
I am currently conducting a survey of all the Steam PSVs in our plant to determine which ones are leaking.
I have tried using a infra-red thermometer and/or thermocouple to measure the pipe temperature under the PSV while also noting the PSV vent pipe temperature. I then use steam tables to convert to gauge pressure and compare this to the pressure set point of the PSV and that of the upstream Pressure Reducing Valve.
My theory is that if the line pressure under the PSV is less than the upstream PRV setpoint then the PSV is passing. If the line pressure is the same as the PSV, then the upstream PRV is passing and the PSV is relieving.
Problem is: in steam lines which have existing pressure gauges the pipe temperature reading is significantly less than the corresponding pressure from the steam tables.
My questions are:
1. Is measuring the pipe temperature an accurate way to determine steam pressure in the pipe or is the pipe temperature always less due to losses, specific heat capacity of pipe etc...
2. What is a typical pipe vent temperature for a PSV which is not passing? Is the conductivity of the pipe such that the temperature of the vent pipe will always be high?
3. Any other methodology/experience regarding determining if PSVs are passing would be appreciated.
I have tried using a infra-red thermometer and/or thermocouple to measure the pipe temperature under the PSV while also noting the PSV vent pipe temperature. I then use steam tables to convert to gauge pressure and compare this to the pressure set point of the PSV and that of the upstream Pressure Reducing Valve.
My theory is that if the line pressure under the PSV is less than the upstream PRV setpoint then the PSV is passing. If the line pressure is the same as the PSV, then the upstream PRV is passing and the PSV is relieving.
Problem is: in steam lines which have existing pressure gauges the pipe temperature reading is significantly less than the corresponding pressure from the steam tables.
My questions are:
1. Is measuring the pipe temperature an accurate way to determine steam pressure in the pipe or is the pipe temperature always less due to losses, specific heat capacity of pipe etc...
2. What is a typical pipe vent temperature for a PSV which is not passing? Is the conductivity of the pipe such that the temperature of the vent pipe will always be high?
3. Any other methodology/experience regarding determining if PSVs are passing would be appreciated.