scythe13
Mechanical
- Jan 3, 2012
- 24
For a warehouse with the dimensions of 170mx117mx12m, a wet pipe sprinkler system must be provided. In NFPA-13, section 5-2 states maximum floor area for a storage to be protected by one sprinkler riser shall be 3716m2
So, in this warehouse at least 6 risers must be installed:
floor area: 170x117=19890m2, min no of risers=19890/3716=5.3~ 6
My question is how many "alarm check valves" this system requires?
Can I just select one 8" alarm check valves with say 8 risers for this system
So, in this warehouse at least 6 risers must be installed:
floor area: 170x117=19890m2, min no of risers=19890/3716=5.3~ 6
My question is how many "alarm check valves" this system requires?
Can I just select one 8" alarm check valves with say 8 risers for this system