Hi All,

I'm trying to model a synchronous generator in SKM PTW using synchronous generator datasheet. I need to put saturated reactances values in pu, however the datasheet provides me reactances in percentage values. Does anyone know how to convert % values into pu values?
Here is my values in %:

aaa_ji9vtn.png


Any help would be appreciated.

Thanks,
 
Replies continue below

Recommended for you

Divide by 100.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips.
 
What xnuke said.

Per cent = for every one hundred
Per unit = for every one

The easiest way to calculate this is to move the decimal point in the percentage value two places to the left; the result is the per unit value.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 
Thanks Crshears and Xnuke for the answers.
I was not sure whether that percentage is of actual value or of pu value. SO it is the percentage of pu value.
 
It is a percentage of the "base impedance" i.e. X_pu = X_actual/Z_base
 
% Reactance is a component of % Impedance.
The full name of % Impedance is;
"Percent Impedance Voltage."
The Impedance voltage is the voltage required to drive rated current through a shorted secondary winding.
Example:
If it takes 3 Volts applied to a 100 Volt winding to drive rated current to drive through a shorted secondary then the PU value is
3 Volts / 100 Volts = 0.03 PU impedance.
3 Volts / 100 Volts x 100 = 3% impedance (voltage)
It is a percentage of the "base impedance" i.e. X_pu = X_actual/Z_base
Uhh maybe add in base KVA, Pythagoras and a factor of 100?

Bill
--------------------
"Why not the best?"