Hello all -
I've got a 40 kW resistive load (heating elements) powered by 480V, 3ph. So FLA = 40kW / (480*sqrt(3)) = 48amps.
I require a contactor for this heating load (ie size 1, 2, 3 etc).
Can someone provide a table or chart that shows contactor sizing based on the resistive load?? I can't seem to find one online or in the NEC. I have the 2011 version of the NEC.
Thanks!! - Phillip