To OP:
I would recommend doing the following:
1) Plot your desired space condition ranges on a psychrometric chart for your elevation
2) Plot your location's summer/winter design conditions (probably ASHRAE climate data in your case or use your company's design day specifications if that is more stringent than ASHRAE)
3) Draw out the process lines required to get from your climate design condition to your desired condition. For example, if I have a -5F winter design day condition, I will first need to preheat say 75F to allow for evaporative cooling to add the required humidity and then re-heat to your desired final dry bulb temp of 70F. This is by no means the only way of doing this process nor does it take into account all the factors that should be considered (equipment overshoot/undershoot/leakage/internal loads/etc) but it at least gives you a mental picture.
To put it in perspective, one of my recent projects was to put a 100% OSA makeup air handler into a cleanroom with a semiconductor industry "standard" of 70F +/-1F, 45% +/-5%RH (note: my application was for 100% OSA, not internal recirc ventilation/cooling). The above thought process allowed me to do ROM calculations on the makeup air handler pre-heat coil, sensible coil, latent coil, humidifier and reheat coil that got me to within 5-10% of the final submittal capacity from our vendor from an afternoon of looking at a psych chart and a little bit of Excel for both the winter/summer design day conditions.
I know the above seems overly simplistic but getting your head wrapped around the situation can do wonders in focusing your research, calculations and vendor info requests on the economics of the equipment that could be applied. In the end, you will likely have vastly different equipment than my example, but the thought process will still be applicable.